    Question

    WE HAVE TWO 600V-347V TRANSFORMERS IN THE PLANT I WORK AT.IN BOTH 347V SYSTEMS, THE NEUTRAL IS NOT GROUNDED.IS THIS RIGHT, SHOULDN'T THE NEUTRAL BE GROUNDED.

  2. #2
    Inactive Member CRM's Avatar
    Join Date
    February 29th, 2004
    Posts
    32
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Rule 10-206 says the system must be grounded at the transformer or the first switch after the transformer. Also read the subsections of rule 10-206. So the neutral would have to be grounded and bonded to the enclosure at either the transformer or the first switch after, but not both.

    <font color="#a62a2a" size="1">[ November 11, 2004 10:21 PM: Message edited by: CRM ]</font>

  3. #3
    Inactive Member bigrockk's Avatar
    Join Date
    September 29th, 2002
    Posts
    146
    Follows
    0
    Following
    0
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quoted
    0 Post(s)

    Post

    Hello Ken,
    A little more info on the paticular system you are taking about would be helpful.

    Check out these links,maybe this applies to your system in question??

    http://www.schneider-electric.ca/www...ml/general.htm

    http://www.ipc-resistors.com/pdf/IPCSTOPLIGHT.pdf